Does this calculation hold for a fan assisted heat emitter? Or does the fan have the effect of extracting more heat from the working fluid?
lawrosa wrote:
So my 200 sq ft camper would need 7000 btu as a heat sourse at a minimum..
200 sq ft x 35 btu per sq ft = 7000
7000 / 550 btu per ft of baseboard @ 180f = 12 ft of base board...( But wait)!!!!!!
I dont have 180f water. And as the chart for heat emmiters goes@ 120F water I would get maybe 200 btu per ft..
so 7000/ 200 btu per ft @ 120f water = 35 ft of baseboard...
Now where the heck will I put 35 ft of baseboard...???