valhalla360
Mar 29, 2016Navigator
Several items change the acceptable length: Generally, you need sufficient voltage at the device you are powering. The longer the cable, the more the voltage drops but there are other factors that can come into play:
- What is the voltage at the pedestal? I've seen everything from 107V to 126V. At the lower end, I would be hesitant to run most anything. At the upper end, you can probably get away with a pretty long cord.
- What size are the conductors in the cable? Most are standard but you can get an upsized cable. Bigger conductors reduce voltage drop.
- What are the power draws? The more amps drawn the bigger the voltage drop. If you are just running the fridge, you can get away with a much longer cord. If you run the fridge, air/con, several lights and get up near the limits, the acceptable length gets shorter.
We have a voltage monitor we plug into an outlet in the kitchen ($25 at home depot). It's easy to see and just stays plugged in. As long as the voltage stays above 110v, I don't worry too much but it's a good idea to check when the air/con or other heavy load kicks on that it doesn't drop too low. It will dip for a second during startup of the compressor but shouldn't go too low and should quickly rebound to 110v or better.
About DIY Maintenance
RV projects you can tackle on your own with a few friendly pointers.4,413 PostsLatest Activity: Jul 22, 2026