tahiti16
Feb 25, 2014Explorer
Unyalli wrote:
The magnum manual states "The AC input and output neutrals must be isolated from each other, do not route the AC input and output neutrals to a common neutral bus." When I take the red leg loose from it's 50 amp breaker and extend it to the inverter with a length of 8/2 wire I would connect the neutral of this new wire to the neutral bus in the picture and the ground to the ground bus. Now with a second new length of 8/2 I would connect from the inverters ac output with the hot (black) going to the right hand 50 amp breaker but where will the neutral go?
Jeff
Where are going to connect the neutral and ground coming out of the inverter? You will need to move the neutral and ground for each of the circuits you are going to run off it to the same neutral and ground as the whole circuit has to be completed.
Easiest way if you can put a small sub box near the current box is feed out to inverter and then into new box and just move the circuits you want powered by the inverter there. You could use the slot that was powering the a/c and micro for a breaker that feeds out to the inverter, this is the way my Dolphin is wired from the factory.