Unyalli's avatar
Unyalli
Magnum 3000w inverter in 50amp system
Hello, If I go the expensive route I will install a Magnum MSH-3012-M Hybrid PSW inverter/charger. I would want the ability to run the entire RV (not all at once of course) via this unit so would have to re-wire. Looking at WFCO's manual for the 8950/30 power distribution panel it looks like the right hand 50 amp breaker powers the breakers to the right of it and the left hand 50 amp breaker powers the breakers to the left of it.
I would have to switch the GFI and water heater so all my outlets were on the right hand 50 amp breaker. Next replace the full width 20 amp breaker for the main air conditioner with a double 20 like the ones way over on the left and reconnect the Ac to one of the new 20 amp breakers and move the micro to the other. Now I would have everything I will ever use on the "red leg" and would wire it through the inverter utilizing it's built in 60 amp transfer switch. Sound about right so far?
I would have all the left hand breakers off all the time as I would not use any of that stuff. I all ready have the ac plug from my refrigerator unplugged so it can never run on ac. The magnum manual states "The AC input and output neutrals must be isolated from each other, do not route the AC input and output neutrals to a common neutral bus." When I take the red leg loose from it's 50 amp breaker and extend it to the inverter with a length of 8/2 wire I would connect the neutral of this new wire to the neutral bus in the picture and the ground to the ground bus. Now with a second new length of 8/2 I would connect from the inverters ac output with the hot (black) going to the right hand 50 amp breaker but where will the neutral go?
Jeff
P.S. I will never try to draw a continuous 3000 or even 2000 watts from my batteries.
Moderator edit to re-size pictures to forum limit of 640px maximum width.
  • RoyB wrote:
    You will need to install several batteries in your battery bank to handle this very large load even for just a few hours. Also when you increase your battery bank capacity then you also have to increase your ON-BOARD Charging system to be able to recharge the battery bank in the desired time you want to the battery bank to return back to a usable charge state.
    Jeff, I missed that part, is this install going in a motorhome, so an extra alternator or bigger alternator is required?
    The Magnum has a 125 amp 4-stage charger, but that only works on shore power, not driving down the road :)
  • Jeff,
    Interesting problem - I guess Magnum wants you to buy two inverters to run a 50a trailer huh? What a PITA!
    I put a separate incoming power panel in a cabinet above my house panel, which feeds the Magnum. Originally I thought I would move my AC and Fridge to it, but decided not to hassle with it. I wanted to be able to run the AC in a pinch if things got really hot.
  • RoyB's avatar
    RoyB
    Explorer II
    Of course what you have described is the so called easy part of your install.
    I think your 3000WATT INVERTER will need around 250AMPS DC Current to operate it at full load which has to come from your battery bank. I notice the spec sheet calls for a 400AMPS DC source to be used. This is some serious capacity requirement.
    Alot of planning will be required in this area as well. The only real time example I can offer from experience is I had to load down a 1500WATT Inverter with test equipment on one Antenna field repair test we were involved with back in my working days. All we had was a rental car with it's single probably a 105AH battery in it. We fired up all of the test equipment was wanting to use which just barely added up to a full load of 1500WATTs. They all fired up normal but only lasted about 15 minutes before running the rental car battery down to a full discharge.
    1500WATTS operated by a 12.3VDC source would represent around a 120AMP DC LOAD (not counting losses). 120AMPS is half the current load of the 3000WATT Inverter so this would drain the 105AH battery in about 7 minutes all things being equal. If you are wanting to run your trailer setup for 8-10 hours like most of us want to do you are going to need many 12VDC batteries in your battery bank... The manufacture wants you to install a 400ADC battery source which will include larger battery cables and a much larger setup to give you a more reliable system to use.
    Just passing along to make sure you are understanding what you may be up against for the 3000WATT INVERTER install.
    Roy Ken
About DIY Maintenance
RV projects you can tackle on your own with a few friendly pointers.4,395 PostsLatest Activity: Oct 12, 2025
