KD4UPL wrote:
You don't need a main. Your main between your power cord and inverter protects on shore power. Your inverter shut down circuits protect on inverter power. Is your inverter even capable of enough power to trip a 30A breaker?
If you really want one then get a 2 space breaker panel like the many that have been shown in this thread, install a "main" 30 in one slot and a tandem 20 in the other. Then wire the output of the main to the input lug of the other buss bar holding the tandem.
From the diagram the OP posted, the inverter was fed from the shore power breaker panel with a 30A single pole breaker.
That would mean that the input of the inverter acts as a 30A "UPS" and would have 10 ga wire from the RV breaker panel.
The output of the inverter (which acts like a ATS) was sending power to TWO different 20A circuits.
IF the OP does not add a small breaker panel to the output of the inverter (IE tie the two circuits together) and the output of the inverter does not exceed 20A (2400W) then the OP will need to DOWN GRADE the 30A breaker. The reason for that is the two 20A circuits from the inverter would be serviced with 12Ga wiring..
OP simply needs a small add on breaker panel, the smallest are "2 space" FOUR circuit boxes which can handle one double pole or 2 single pole standard size or 4 half size single pole breakers..
These panels do not have "main" breakers, instead they have INPUT LUGS.. Cost shouldn't be much more than $12 for the small panel..
Looks like this..

This one is 11" tall and 6" wide..
Found
HERETakes standard easy to find breakers (but if you use two standard single pole breakers you will need to "jumper" the two lugs feeding the breakers from the inverter together).
Best bet is to go to the store and see what they have available, many times they have other versions than what is listed on the website. You might wish to check Lowes also if the panel at Home Depot is too large.
IF new panel will not fit where the old inverter was you can move the location of the new small breaker panel by using 10 ga wire from the inverter to the new breaker panel location.. That keeps things inline with the 30A breaker feeding the inverter.