dieseldan723 wrote:
This is what the panel says:
Power Converter System - PD4590K18L
Input: 105-130 VAC. 50 - 60 Hz 1550W
Output: 13.6 VDC. 90A
Class CTL Distribution Panelboard
Type 1 Enclosure (indoor) 812385A
Does this give you what you need? I wish I was a better electrician. I am pretty handy with mechanical things but electrical issues just aren't my thing....yet!
This is a Progressive Dynamics 50 amp distribution panel with a 90 amp converter charger with built in charge wizard. This should serve you very well.
The charge wizard should apply 14.4 volts for up to 4 hours to fast charge even a large set of batteries. The only issue would be to check voltage when the batteries are down. As the charging starts the voltage should ramp up within 20 minutes to be over 14.0 volts.
If not there is a button and indicator light to change to boost mode manually.
http://www.progressivedyn.com/pdfs/110030%20English.pdf
You should never have to run the generator more than 4 hours to get a 90% charge. The last 10% will take an additional 4 to 10 hours so save that for when you are plugged in.
http://www.progressivedyn.com/all_in_one_pd4500_1.html