allen8106 wrote:
LOFAT36 wrote:
I wonder why they put floor vent's in the bathroom & bedroom in 5ers, especially the kind that I have that don't close. We all know that heat rise's so while I'm comfy sitting downstairs my Lady is dying from heat in bed. Anyway I just blocked those 2 off with foil tape so we'll see how that shakes out.
This will cause the furace to run too hot and will eventually damage the heat exchanger.
High temp limit switch should shut down furnace .... they range from 130*F to 190*F set points depending on furnace btu rating.
Furnace would probably 'short cycle' if not enough air flow due to too many registers closed off.