barberbunch wrote:
Does anyone know if any RVs with an electric heat option ever had a different set-up than a heat pump?
RV Heat Pumps started in 1999. Before that NO HP on a RV roof top unit. Prior and NOW, roof AC's have always had a HEAT STRIP option. What this is, is, a 5600 BTU 120 volt electric heat coil on top in front of the AC evaporator.
REGARDLESS, if you have a roof top HP or a roof top Heat Strip, the roof AC fan MUST run for either system to work.
The difference between a Heat Strip(5600 btu) and a HEAT PUMP is, the HEAT PUMP will have the BTU rating of the roof AC (13500 btu or 15000 btu). MORE heat capacity. BUT, HP's will NOT work below 36 to 38 degrees outside ambient temp. HEAT STRIPS will work, but they only put out warm air to take the chill off, they will NOT heat an RV.
Now, from your previous response about you NEVER had roof top air flow on your "heat" option only thru the floor vents. Carriage did not install a hybrid system. IF you had a TRUE HP before, it all depends on the BRAND of the HP. Coleman(RVP) or Dometic. Coleman roof HP's have a design quirk built into the logic. When in HP heat mode, IF you set the wall tstat MORE than 5 degrees from the inside temp of the RV, the Coleman system will activate the LP furnace and the furnace will heat the RV. Once the interior temp is LESS than 5 dgrees of that set temp of the tstat, the furnace kicks out and the roof HP comes on and heats the unit up to preset temp. Dometics do not have this design. SO, if you indeed had a HP originally and your only heat came from the LP furnace, your system has never functioned as designed.
There IS a COST difference between a HP and a COOL only roof top AC unit. HP's cost more. Doug