Just a curious question for all you experts out there, We have a 2002 32V Itasca Sunrise, bought it used, have had it almost 2 years. It has the 30 amp power cord, however, the box the power cord goe...
It would not be all that difficult to install a new 50 amp power panel in a basement compartment, with a 30 amp breaker feeding the existing power panel, and 20 amp breakers feeding both A/C units. Then you will barely have any power on the factory 30 amp panel, the rest will be OK.
Then you will only need to run the #6-4 wire to the new panel, and run the factory cord to the new panel's 30 amp breaker. This would allow running 'everything' while in a 50 amp park.