Executive45
Jun 06, 2019Explorer III
Whoa Kimo Sabbe! It's a bit more complicated than simply replacing a breaker and receptacle. That is unless your home fire insurance is paid in full, you no longer like your house, and the insurance company won't find you at fault for frying all the wiring inside your box. Generally, 20amp service, (Tee shaped receptacle) uses 12 ga wire, 15amp service (Double I shaped receptacle) uses 14 ga wire. 50amp service uses a minimum of 10ga wire, depending on the length of the run. Simply changing out the breaker and receptacle will allow you to power up you A/C units for a bit as your breaker will not trip. However, your house wiring will then become a substitute for your breaker. Once the wiring gets too hot, it will melt and burn through if you're lucky. If you're not so lucky, it'll simply start a fire and burn your house down. Hire a licensed electrician....Dennis