- PastorCharlieExplorerMoving plug in and out = wear = loose connection = resistance = heat = burn.
1500 watts X 2 = 3000 divide by 120 volts = 25 AMPS..... ON 30 AMP service breaker will trip at plus 30 AMPS
Problem appears to be resistance not load. - MrWizardModeratorTwo heaters on high use 24 amps, from a 30 amp circuit
That leaves 6 amps to power everything else, tv lights, charging, MW coffee maker ?
Yes something has got to give
And you see the results
Time to turn off one electric heater and burn some propane for heat
Or you will continue to have problems and burn up the new cord ends - rozrob2000ExplorerScott: I am new to this. Yes everyone has been helpful. When I posted on the other, I did not realize it went to Forum Technical Support. My mistake. I sincerely apologize to all for the inconvenience.
- ScottGNomad
pianotuna wrote:
Hi,
Low voltage in the grid can cause you to draw more amps. Poor connections cause heating which makes the connection worse, which causes even more heating.
True in cases of motors or any regulated item but not in a resistance space heater. Reducing the voltage to it results in less current, not more. - pianotunaNomad IIIHi,
Low voltage in the grid can cause you to draw more amps. Poor connections cause heating which makes the connection worse, which causes even more heating.
Replace the cord end.
Also replace the female outlets in the RV that are being used for high wattage appliances. - ScottGNomadThe receptacle is worn to the point it can no longer carry that much current. Or, there is a failing connection inside your plugs head. Bad recept's are rather common with 30A receptacles though.
Did you not like the answers you got on your other thread of the same thing?