Ivylog wrote:
Park changed the 50A breakers and the new tripped too. Two ACs and a Aqua Hot with 2 electric elements will overload most systems.
The mode 600D has 2X 2000W heaters. 16.7A + 15A A/C = 32A.
That leaves 18A on each leg which is certainly manageable. Of course if he has other high draw appliances and uses them all. Or the loads aren't balanced on the 2 hots. :h
He could turn off the A/C heat pumps and use just the Aquahot on electric and diesel. :S If the A/Cs are for cooling then the Aquahot would be for hot water only and the situation is even more managable. We turn on ours for hot water and then turn off. And of course leave it on when used for heating.
There is more to this story...