hipower wrote:
Clay L wrote:
hipower wrote:
Clay L wrote:
Does anyone know what pressure is required to cause venting? With that info one could use the Ideal Gas Law to calculate the temperature at which venting would occur.
SNIP
The vent pressure of most LP tanks is 250 psi. Some are built to a comparable standard and have a rating of something around 300+/- psi, but were intended for propylene service, not propane. I mention this only because I have seen those tanks repurposed by unknowing individuals and it causes an undue risk in propane service due to the higher relief valve setting.
I found a chart that shows that propane at 80 F will have a pressure of 140 psi. Using the ideal gas law I found that the temp would have to go to 500 F before the tank pressure reached 250 psi. That seemed high and even though the calculation is simple I used a couple of on-line calculators and got the same answer.
The chart is HERE and one of the calculators I used is HERE
So unless I did something dumb (that's always a possibility) it doesn't appear that an enclosed compartment, truck or car interior is going to get hot enough to cause venting.
The variable that you must consider is when someone overfills the cylinder. A little rarer today with the OPD valves required, but they are mechanical float devices that can fail. They can also be overridden by a high pressure/volume filling pump like those used on propane delivery trucks. One of the reasons suppliers don't want to fill smaller containers from their bobtail trucks.
If you want to check that your tank is properly filled simply look at the data on the collar of the cylinder. The tare weight of the cylinder will be there along with the WC (water capacity) number. Tare is obviously the empty weight of the cylinder while the WC times .42 provides the capacity of the cylinder in pounds of propane. Add the two numbers together and you will have a total weight for a full cylinder. Eg: a 20# cylinder with a 18# tare weight and 47.6 WC will weigh 38# full. Anything over that is overfilled anything less obviously is underfull.
Many of the exchange companies have established policies of underfilling to avoid liability issues with overfilling by minimally competent fillers. We frequently see these cylinders at 15-18# of propane when filled. This is only an issue when it comes to filling your cylinders more often or if you are paying a price equal to an actual 20# fill. Then it is a rip-off.
Shouldn't be a big problem because usually the supply tanks are above ground and would be very close to the ambient temperature. Although you will find some supply tanks underground, most are above.