Forum Discussion
hotjag1
Jun 21, 2019Explorer II
Generac service center did a lot of testing and determined that when the GEN was under heavy load (AC) the voltage regulator would get warm and the voltage would increase. When that happened an internal resetting circuit breaker would open and cut power output from the GEN.
The voltage regulator under lighter loads such as coffee maker or microwave wasn't drawing enough power to heat up the voltage regulator as this only happened with the AC on. They replaced the voltage regulator and ran the AC for over an hour and everything worked as designed. $100 labor and $100 regulator and so far, so good.
The voltage regulator under lighter loads such as coffee maker or microwave wasn't drawing enough power to heat up the voltage regulator as this only happened with the AC on. They replaced the voltage regulator and ran the AC for over an hour and everything worked as designed. $100 labor and $100 regulator and so far, so good.