VA-Apraisr wrote:
Assuming to install 2 a/c units, you would have to have 50amp service??
If they're of any size, (BTU's), then YES. The option of two 11,000 units, just thinking without checking, would not run both on 30A. Two 8,000's? Sure, but WHY?
There are Load Shedding devices, but they mean two won't run at once. And I'm sure two 13,500 units won't run on 30A. Friend had a 33-ft Class A that was 30A shore tie and a 5500 Watt Genset. Could run two A/C on the Genset, but only one on Shore Tie.