laplatarosa wrote:
I have a large DP with an installed Surge Guard Plus Model 40250-RVC Automatic Transfer Switch with RV Power Protection 120/250V 50A, 60Hz.
The coach does not want to hook-up to a 50amp , receptacle that is showing L1 - 124v, L2 - 127v, LI to ground & to neutral - 124v, L2 to ground and to neutral - 127v. L1 to L2 - 252v.
The generator connects and works fine. Also the auto Genset start works as designed.
I CAN connect to a 30 amp receptacle via a dog-bone adapter on the L1 -124v side of the pedestal.
The specs for the Surge Guard say below 132v range is OK.
Any ideas why I cannot connect to the 50amp power.
I'm using the same cord for all connections.
Thanks in advance for all ideas.
LaPlataRosa
It's probably sensing a problem with the neutral or ground. I believe if it measures any current flow in the neutral wire, it won't allow power to go to the RV.
See if you can use a nearby 50 amp outlet (assuming you're in a RV park).
PS I had the opportunity to open a Surge Guard device a few years ago to check it out and I wasn't impressed by their quality. Don't discount the possibility that you have a bad one.