SoundGuy wrote:Lenny K wrote:
Does this setup work for 50 amp if you use a 50 amp adapter?
50 amp RV service is actually 100 amp service consisting of 50 amps across each of 2 legs so obviously if you wanted to check both legs you'd have to use 2 monitors. The simpler and better solution for those who have a rig wired with 50 amp main service is to invest in a 50 amp EMS which is designed to check & continuously monitor both legs of that 50 amp service.
Basically correct, but it's inaccurate to call it a 100A service. It is a 50A 120V/240V split phase service. None of the wires or connections ever have 100A flowing, and you don't need wire sized to carry 100A, and you cannot power a single 100A 120V device should you happen to have such a beast. You can use up to 50A at 240V, or have two legs of 50A at 120V, but not a single leg at 100A.
Similarly, a semi tractor pulling dual 28' trailers is not a truck with a 56' trailer. The two are far from equivalent if you have some 35' long pipes to haul.