myredracer
Apr 18, 2018Explorer II
Lynnmor wrote:Excellent question and one I have tried to find the answer on in the past. Unfortunately, RV AC makers do not publish any data on current draw versus voltage so can't give a reasonable/accurate answer. Couldn't find a graph of some kind either that would demonstrate what happens, even on a generic residential air conditioner.
Gil,
Could you give us a good estimate of power usage between an AC laboring on 100 volts, and an AC operating more efficiently on 110 volts boosted by an autoformer? Of course the one on low voltage may well burn up.
The mechanical load on a compressor motor stays basically the same so as the voltage drops, the current will increase as the motor works harder to produce enough power to drive the compressor. In approximation, I would say that there isn't a significant difference in power consumpution. I think the autoformer has an internal loss of something like 3-5%.
The big difference is in damage that occurs as voltage gets low. HP output of the compressor motor will go down as the square of the voltage (running condition). At initial startup, the torque will drop as the square of the voltage. Both of these cause overheating of the windings and damage to the insulation. At some point as voltage drops and current goes up, the 20 amp breaker can trip or the overload element will (due to overheating windings) and if either occurs you want to check voltage. Momentary startup current can be in the 60-70+ amp range depending on model/brand of AC unit which is around 5 times full load running amps. You *could* be at a reasonble but low voltage while running but the voltage can drop out of sight on startup due to how the CG is wired. You can't see what happens to the voltage on startup and will never know harm it is doing.
Dutch_12078 wrote:
I don't use an autoformer, nor have I run across a park to date where I needed one, but in those that prohibit them in their rules, I've found the predominate reasons are that they believe the devices somehow "steal" power, although I've never found a park manager or owner that could logically explain how that happens. The other reason has been possible liability insurance issues because the NEC prohibits the use of auto(trans)formers in RV's, which it does. I have inquired of the NFPA what the reasoning is behind the prohibition a couple of times, but I've never gotten a response.
Note that the NEC only covers permanently installed electrical wiring & components installed within RVs by RV manufacturers. It is perfectly fine to use a plug-in autoformer. Oddly, extension cords and adapters aren't required to be UL listed (which is why CW sells non-listed ones). The Hughes autoformer as a complete unit isn't UL listed and only has internal components that are. You may not want a hardwired piece of equipment in an RV that isn't UL listed... I think I know why the NEC doesn't allow them but would be speculation on my part.
The autoformers do NOT steal power in any way, shape or form. It's scientifically impossible. If there were many users in a CG using autoformers, it is theoretically possible to increase current in feeders and the main service to the point that a section of a CG or the entire CG could be overloaded. When the current goes up, the voltage goes down so the power being used is the same or less. Plus, many autoformers would drag down the voltage throughout a CG. However, the reality is that there are very few RV-ers in CGs using autoformers.
Curious what CGs/RV parks people stay at where you don't run into low voltage? Do you monitor voltage with a permanent voltmeter mounted inside?
Looking for advice before your next adventure? Look no further.25,214 PostsLatest Activity: Sep 19, 2026