Furnace Cycling - SOLUTION w/ Pictures
EDIT: This turned out to be an air flow issue. The solution was quite simple. The furnace has three knockouts on the back when using flexible vent duct adapted to hard in-floor ducting. Crossroads has only used two of the three ducts, so I knocked the third one out, moved the lower two so they ducted in to the floor and ducted the top one so it ducted in to a 4" adjustable vent blowing directly in to the kitchen.
Pictures:
The stock furnace access panel/cold air return:

Access panel removed:

Duct disconnected from floor:

This shows duct connected to new access panel/cold air return:

Access panel sitting on floor:

Access panel installed:

All I have left to do is seal a couple spots a bit better with duct tape and stain the new access panel I built to match the interior of the TT.
So, if you've got a Crossroads Zinger ZT33BH and are having furnace issues, this may solve them for you. Grand total for materials was $40 for the lumber, and my dealer provided all the ductwork and fittings for free (since it should have been a warranty issue, but I couldn't get them to do a service call to where my trailer is located).
Pictures:
The stock furnace access panel/cold air return:

Access panel removed:

Duct disconnected from floor:

This shows duct connected to new access panel/cold air return:

Access panel sitting on floor:

Access panel installed:

All I have left to do is seal a couple spots a bit better with duct tape and stain the new access panel I built to match the interior of the TT.
So, if you've got a Crossroads Zinger ZT33BH and are having furnace issues, this may solve them for you. Grand total for materials was $40 for the lumber, and my dealer provided all the ductwork and fittings for free (since it should have been a warranty issue, but I couldn't get them to do a service call to where my trailer is located).
Brand new 2013 Zinger ZT33BH, and the furnace is misbehaving:
1.) Thermostat calls for heat
2.) Furnace fan starts
3.) Burner ignites
4.) Runs for ~2 minutes then stops, fan continues running
5.) burner ignites again
6.) Repeat steps 4 and 5 until:
7.) thermostat is satisfied and furnace shuts down normally
My only guess is a bad high limit or sail switch, but I'm not a furnace guy. Should still be covered by warranty, but I'd like it fixed in place instead of hauling it to dealer (I'm all set up for the season, don't really want to move).
Anyone else have/have seen this issue?