Yes, you can easily have 30 and 50 amp at the same pedestal.
You will be pulling 4 wires (what kind and gauge dependent on length of run, above/below ground, etc).
Your 50 amp will have: two hots L1 and L2 (240 vac between them), one neutral and one ground.
Your 30 amp will use just one of the hots (if more than one pedestal, alternate using L1 and L2), one neutral and one ground.
You will be pulling 4 wires (what kind and gauge dependent on length of run, above/below ground, etc).
Your 50 amp will have: two hots L1 and L2 (240 vac between them), one neutral and one ground.
Your 30 amp will use just one of the hots (if more than one pedestal, alternate using L1 and L2), one neutral and one ground.