no. a 20 amp breaker on a 12 amp load should not be hot. You have a loose connection or loose breaker on the buss bar.
I don't know. I really don't. But I'm thinkin the AC pulls more than 12 amps.
Starting, yes. Running, probably not generally, or at least not a lot more. 15 kBTU and 12 A works out to an EER of 10.4, which sounds about right. 13 A running would not surprise me. (EER is BTU per watt under some test conditions; SEER is the same, with a specified set of varying test conditions in an attempt to simulate a "cooling season".)