KD4UPL
Jan 08, 2014Explorer II
john&bet wrote:
The safety of the idea has not been address yet so let me be the first. You have the potential to overload the neutral of the adapter or the neutral of the recptical or the neutral anywhere up stream of that point. If both 30 amps are loaded to say 24 amps then there is 48 amps on the neutral which will be pushing it and the connections. JMHO.
With 24 amps on each leg you will have 0 on the neutral. Overloading it is not a concern. The most you could possibly put on the neutral would be 30 amps. This would occur with a 30 amp load on one leg and nothing on the other.
And no, a 50 A circuit does not have 2 neutrals.