The FIRST thing that needs to be done is verify that you do INDEED have TRUE 50 amp service. Take a voltmeter and check the voltage between the 2 hot leads at the CG 50 amp plug. It should be 220/240 or double the line voltage. IF it does not read double, then you are NOT on 50 amp service(100 AMPS TOTAL) but on a single phase 50 amp breaker. This would be the cause of your PI dropping out. Also a loose NEUTRAL at the CG power receptacle may also cause voltage problems with full 50 amp service. Doug