Forum Discussion
CA_Traveler
Oct 02, 2014Explorer III
dougrainer wrote:It's not 50A RV power but that will not cause the PI unit to drop out. 0V between the 2 hot legs is OK and it's a necessary design constraint in order to be transparent when using a 20A or 30A power with adapters.
The FIRST thing that needs to be done is verify that you do INDEED have TRUE 50 amp service. Take a voltmeter and check the voltage between the 2 hot leads at the CG 50 amp plug. It should be 220/240 or double the line voltage. IF it does not read double, then you are NOT on 50 amp service(100 AMPS TOTAL) but on a single phase 50 amp breaker. This would be the cause of your PI dropping out. Doug