What is your application? - pianotunaNomad IIIHi Enblem,
The application is to remove the fuddy duddy (me) who plugged a 600 watt oil filled heater into a 400 watt inverter which was connected to a 15 amp cigarette lighter outlet.
I had just completed a 15 hour drive and was so tired I could hardly see straight. - MEXICOWANDERERExplorerKnow the feeling...
Voltmeter was rearranged by housekeeper during my 5 day absence. 13-hour taxing ordeal. Jumped into bed, glanced at the red numerals and my hair stood on end. Meter was downside up. - I do not think what you are planning is the correct way to go.
400 watt inverter would draw around 35 amps at 12 volts.
600 watt heater would draw around 5 amps at 120 and ten times that for 12 volts DC.
Installing a circuit breaker trying to protect your self from your self doesn't seem appropriate. No offense! - BFL13Explorer II
CA Traveler wrote:
pianotuna wrote:
Let's see: 400W/12.7V = 31A. Really? Dam* right you should not!
My need is quite simple. I run a 400 watt inverter from a cigarette lighter plug (ya I know, I should not).
Why not do it right?
EDIT--actually using the divide by 10 rule, that would be 40 amps.
If all he usually runs from the 400w inverter pulls less than 8 amps DC, then why not? IMO (not shared by some here it seems) it is the size of the load that counts, not what the inverter "could do" from its rating.
If PT puts too big a load in that inverter, then the 10 amp "TV Fuse" in his DC fuse panel that is for the Winegard 12v socket and antenna booster will blow. Which is what happened.
What's the big deal? - This is worse than I imagined....
I don't think a CB is the solution. - BFL13Explorer IIIf the inverter was loaded enough to pull more than the size of the fuse in amps, so it blew the fuse, you would not want an auto- resetting CB in there to keep popping and resetting.
A CB that did not auto-reset could work I suppose, but there is maybe a timing issue in how long it takes or how hot it has to get to pop compared with a fuse? - pianotunaNomad IIIThe usual load is a laptop and a heating pad. Total less than 100 watts.
The outlet has a 15 amp fuse at the panel and nothing else is on the circuit. Because I've been running in this manner since 2009, I don't think overload is a serious problem.
The fuse did exactly as it is intended to do and blew immediately. Replacing it is down on my hands and knees using a flashlight to attempt to see which fuse has failed. There are labels but they are cryptic.
At least the maker used a decent size of wire, but the choice of location is definitely less than convenient. - OK lets get an 80w inverter for the 12v outlet, proper 50a connection to wire in that 400w inverter, and some better labels on the fuses.
Besides why not just use the magnum? - pianotunaNomad IIIThe overhead on the Magnum is about 40% of the load. So instead of using say 5 amps I'd be using 10.