BB_TX wrote:
valhalla360 wrote:
Probably yes...until the cord melts. As skibine showed, you are probably looking at 27-30amps in ideal conditions. A 30amp is rated for 24amps continuous load.
......
Please show me the specifications that show a 30 amp cord is only rated for 24 amps continuous. I really want to know.
I suspect that was in literal sense..
Cord and plug will get pretty hot, the plug most likely will heat up enough to soften the plastic holding the pins when full load is applied for long periods of time..
But, from the breaker point of view, yes, it is very possible that running more than 24A on a 30A breaker continuous can cause the breaker to trip before 30A.
The breakers used are thermo-magnetic trip, the thermo part creates a small amount of heat under loads near the rating.. Do that long enough and the breaker will trip due to thermal overload. The small amount of heat generated inside the breaker never has time to dissipate under continual loads and that increases the chance the breaker will trip under lighter loads than at rating.
Thermo trip is slow and takes time (think of it as a time delayed blow) but magnetic trip is for those very fast current spikes like what happens when you have a short.
I have seen 16A-18A loads on a 20A breaker run for a long period of time trip the breaker..