BB_TX wrote:
Sorry, but I don't use a 50 amp cord on 30 amp service. I use a 25' Marinco 30 amp power cord with a 50 amp connector on the trailer end and a 30 amp plug at the shore power end instead of my 50 amp cord with a 50/30 dogbone.
In your case, the 30A breaker on the shore power side OR generator breaker will pop before your 50A main breaker, therefore protecting your 30A shore cord from overload..
But once again, the 30A breaker or even the breaker in your gen are thermal/magnetic trip. The thermal trip once you get to 80% continuous for more than a couple of hrs will trip much easier as the breaker warms up.
You shore power cord even though it may be 10ga and rated for 30A, does indeed dissipate heat as you draw power, the more power drawn, the more heat it must dissipate.
The same insulation that protects you from touching live electrical wires becomes a insulator of heat. Making it difficult for the copper wire to dissipate any heat build up over time near full current rating. So, it is normal for a continuous heavy load to heat up your shore cord more than enough it will be warm to touch.
Uninsulated wire can handle more current for a longer time than insulated wire in the same wire gauge.
Heat dissipation and heat build up are the reasons why non insulated open air 10 ga wire can handle more current over a longer time than 10ga wire with insulation..