You do not understand. I want to increase my controller presently at 40 amps output, to 80 amps. With my controller output at 24 volts i can do this. But then my battery bank has to be 24 volts. So i need to convert this to 12 volts for my inverter-charger
Amps at 24v is half the amps at 12v.
Your output amps come from the output watts. You divide the output watts by the battery voltage to get your amps.
Here is how it works 24v-12v. Your 600w array might be putting out 540w on a nice day. ( You lose about 10% due to panel heating in the sun--those panels get hot.) You lose another percent or two on the wires going to the controller's input. So input watts might be 540 -11 = 529w
So you have 529w on the input with the controller doing say 30v at Vmp ( example) so the input amps is 529/30 = 17.6a. (wire gauge for that) The controller efficiency is say 96%, so output watts is 508w.
Now your batteries are starting in the morning at say 12.5v, so they will get 508/12.5 = 40.6 amps --wire gauge for that-- (but the controller rated at 40 will keep the amps at 40, not letting the amps get higher.)
Later after the batteries are recharged some, their voltage is now 13.5v rising, so amps now (assuming same watts--actually with higher sun at noon watts might be higher--depends if panels are flat or aimed at sun all day) anyway 508/13.5 = 37.6a
As battery voltage rises, amps go down with the same watts.
With the 600w you are slightly "over-panelled" for that 40a controller, but that is a good thing for your over-all daily AH haul since you will get to use all the array can do earlier and later in the day when the sun is lower.