BB_TX wrote:Bobbo wrote:
...........
In this case, there is no 50 amp neutral. The 30 amp neutral definitely can be overloaded, if the 30 amp and 20 amp outlets are not fed from the same main breaker, but are still on the same leg.
.............
Actually there is a 50 amp neutral all the way from the RV load center to the end of the 50 amp cord where it would plug into the adapter. Then the neutral splits into a 30 amp neutral to the 30 amp plug and a 20 amp neutral to the 20 amp plug. And those two neutrals would connect inside the pedestal.
There is no 50 amp neutral from the pedestal to the main box feeding it. That 30 amp neutral can be overloaded too.