What actually happens is a bit more complicated. Try thinking about it this way. You have 30 amps at 120 volts available at the breaker panel. 3600 watts. Now if you were really close to the panel, you would have almost that much left for your griddle and A/C. When you have things in series, you have voltage drop. In your case, the things you have plugged in in the camper is one thing, and the wire feeding those things is another. So, the voltage drop along the feed line becomes important. As your current draw in the camper goes up, the voltage drop in the wire feed goes up as well. So, perhaps out of the desired 120 volts, you only have 100 left.
So now your A/C starts up, and it's motor needs 120 volts to run well. It's only getting 100. It tries to run, but the current goes up, and the wires feeding it get hotter, and the voltage drop in the wires gets larger, until finally your A/C motor and fridge motor burn out.
So, how to fix it? Well, adding a 50 amp breaker will most certainly cause real damage. The only way to ensure you have adequate voltage at the camper itself is to increase the size of the feed wires. That gets expensive fast, but will solve your problem.
If you have 30 amps in a No 10 wire for 300 feet you are losing almost 18 volts in the wire. If you go to No 6 you are only losing 7 volts, and No 4 is only 4.5 volts. That is your solution. And I am an electrician.