30 amp to 50 amp Conversion

My home RV parking spot was wired with a 30 amp RV service. My new RV is 50 AMP. I used a dog bone adaptor for a few days but wanted to run both AC's.

I noticed the that the 30 amp breaker was a double pole breaker. I removed the cover to find only one pole was being used AND there was an un-landed taped off extra wire. The unused wire was also taped off at the RV box. The builder had ran 10-3 W/G romex to the RV subpanel. Great. I had already purchased a 50 amp RV panel in anticipation of running another service.

I removed the 30 amp RV box and installed the 50 amp box using all 4 wires. I landed the unused hot on the breaker unused pole, leaving the breaker at 30 amps because it is still #10 wire.

I have created a 30 amp 220V service capable of 7200 watts as opposed to the standard 50 amp 220 service capable of 12000 watts. It is far better than a 30 amp 120V capable of only 3600 watts that I had.

I made voltage checks with the meter and plugged in the RV. I started both AC's and an amp check showed 13 amps on one leg and 15 amps on the other leg.

Does anyone see a problem with this? I do plan to run #6 wire but it will take some time and planning as it will have to be in conduit on the outside of the building. But for now all is working well. Heck, I may leave it that way if it never trips the breaker.

I don't see the need for 50 amps anyway. The generator is only 5500 watts and it runs both AC's. I am guessing it is a 20 amp 220 v service.

8 Replies

  • Excellent job and qualifies for a pat on the back. ;) Perfectly safe since the breaker upstream of the #10 wire is 30 amps.

    Unless you have tripping issues, you probably won't ever need to upgrade. What does the voltage inside your TH look like? Should be measured with both ACs running and also maybe at the hottest time of day if neighbors drag the voltage down in the neighborhood from them all running ACs at the same time. If you don't have one, it's always a good idea to have an EMS unit to protect ACs against low voltage.
  • CJW8 wrote:
    My home RV parking spot was wired with a 30 amp RV service. My new RV is 50 AMP. I used a dog bone adaptor for a few days but wanted to run both AC's.

    I noticed the that the 30 amp breaker was a double pole breaker. I removed the cover to find only one pole was being used AND there was an un-landed taped off extra wire. The unused wire was also taped off at the RV box. The builder had ran 10-3 W/G romex to the RV subpanel. Great. I had already purchased a 50 amp RV panel in anticipation of running another service.

    I removed the 30 amp RV box and installed the 50 amp box using all 4 wires. I landed the unused hot on the breaker unused pole, leaving the breaker at 30 amps because it is still #10 wire.

    I have created a 30 amp 220V service capable of 7200 watts as opposed to the standard 50 amp 220 service capable of 12000 watts. It is far better than a 30 amp 120V capable of only 3600 watts that I had.

    I made voltage checks with the meter and plugged in the RV. I started both AC's and an amp check showed 13 amps on one leg and 15 amps on the other leg.

    Does anyone see a problem with this? I do plan to run #6 wire but it will take some time and planning as it will have to be in conduit on the outside of the building. But for now all is working well. Heck, I may leave it that way if it never trips the breaker.

    I don't see the need for 50 amps anyway. The generator is only 5500 watts and it runs both AC's. I am guessing it is a 20 amp 220 v service.


    I have occasionally recommended doing exactly this to save a little on costs. that is assuming you won't be living in the RV in the desert.
    bumpy
  • I has been years since I put in my 30 amp 120 plug but i foggily recall the the #10 was good enough for the 30 Amp, just as yours was wired also.

    It would look like to me that if you put another #10 in service to complete the 220, you could just run it as is with the double pole 30 breaker like others have indicated.

    But I did not get my book out or ask google. :h
  • Unless the breakers are blowing, I would not bother running the #6 wire.
  • smkettner wrote:
    A 50 amp outlet really should be 40 or 50 amp service to meet NEC afaik.
    No safety issues and I would run it as is.
    OP, With the breaker the appropriate capacity for the wire size I see no issue whatsoever.
    Good move!
    My "50A" outlet is fed from a 40A breaker as I ran 8/3 wire, not 6/3.
    More than I need at home anyway.
  • A 50 amp outlet really should be 40 or 50 amp service to meet NEC afaik.
    No safety issues and I would run it as is.