Almot wrote:
12thgenusa - hitting 30A post-controller with 360W panel is extraordinary. Max panel output is normally no more than +/- 3% from nominal, if there is any QC at the factory.
360W @12.6V = 29.5A max at standard conditions (70F? don't remember), even if you got +3% more power than you paid for, zero loses in cables and 100% controller efficiency. In other words - unless battery voltage is less than 12V, this can not happen. Maybe it was some "sleep mode" or other effects? Was it unusually cold or at high elevation?
PS: correction, it's minimum 13.6V (or whatever your setpoint is). I don't see how you could get more than 25A current with 360W.
Several things. It's two 185-watt panels for 370 watts, not that that matters much. Elevation is usually above 8000 ft. Generally cool temps in Colorado mountains (60-75F). Panels tilted for optimum output.
From the data log on the Rogue I have seen over 400 watts more than a few times. The highest that I remember was 411 watts. Since the 411 watts is measured at the controller I assume wire loss is already accounted for. If you assume a controller efficiency of 96% the maximum voltage to reach 30 amps is 13.2v (411*.96/30=13.15). I quite often will operate a high demand appliance during the day; MW, coffee maker, hair dryer so voltage will drop well below 13v.
If one limits the use of solar to battery charging only, it is a different story. By mid-day when panels are at max, battery voltage has risen to the point that 30 amps is no longer possible.
For the OP at 460 watts a voltage of 14.6 or less will hit the 30-amp max. (460*.96/30=14.56)