troubledwaters wrote:
BillyBob Jim wrote:
At the campground I am familiar with its not going to work. It will work from the standpoint that you will power up both legs of your 50 amp system, but you're not going to have more than 30 amps.
The main feed is 30 amp, the 20 amp receptacle is tapped off of that 30 amp feed. They did not run a separate/independent 20 and 30 amp feeds to the pedestal. If they would of done that they would of simply installed a 50/30/20 pedestal and if they would of, that would not mean you can somehow dog-bone 100 amps out of it.
Please let me know the name and location of this place; I want to make sure I never get close to there. The place sounds like a nightmare with duct tape and baling wire-cobbled up electrical panels and probably everything else.
Wonderful, don't get close to there. Just so happens to be a state park with everything duct taped and bailing wire tied together lol, wired all 30 amp pre 1980. I expect you only stay at brand new high falutin resort type places where everything is brand spanking new? You'll find the same situations at a lot of State and Fed facilities if you open your eyes.
For the RVnet code fetish club, you haven't a clue what, or what version, of a code was in effect when park A, park B, or park C's system was installed.
Popcorn a poppin.