Not familiar with this protector but I think it is seeing an error on L1 and L2 being in phase.
To get the 100 amp service you have:
L1 50 amp
L2 50 amp
Neutral 50 amp
L1 and L2 together give you 100 amp service.
Normally L1 and L2 are out of phase so neutral never sees more than 50 amp
If L1 and L2 are in the same phase, then neutral could be forced to carry up to 100amps, but is only rated to carry 50 amp. Since neutral is not circuit breaker protected, a potential overload exists. No circuit breaker will trip, but you might smell rubber burning.
The camp worker using a volt meter would not be able to detect any error.
If that's what it is doing, then, that is a very good device indeed.