ScottG wrote:
It may already have fuses.
Some inverters do, and some do not.. Those that do, the fuse is for reverse polarity protection or catastrophic overload protection of the inverter..
The built in inverter fuse has nothing to do with protecting the WIRE from the battery to inverter.
The rule of thumb for ANY voltage source is to FUSE (breaker or fuse) your wire AT THE SOURCE ON POWER. Typically within 18" of the battery..
You ALWAYS fuse OF THE WIRE TO NO MORE than the max SAFE current..
You can underfuse but never exceed the allowable safe current.
For instance 12ga wire can handle 20A, you either fuse to 20A or you can fuse to 15A or less.. But don't fuse to 30A!
The idea is if something happened that the wire insulation was chafed and a short develops along the wire the fuse will blow before the wire gets hot enough to cause a fire..
The fuse also protects the wire from overload of the wire due to excessive current drawn from the load..