Dutch_12078
Mar 24, 2019Explorer III
wnjj wrote:Dutch_12078 wrote:
Those "50 ampers" cannot pull more than 30 amps through the 30 amp breaker, and 15 or 20 amps using a separate cord plugged into the breaker protected GFCI utility outlet. None of the 'Y' adapters, whether commercial or homemade, will work with an NEC compliant park panel.
The larger RV’s are more likely to max out the 30A and also may want to use the 20A at the same time. Many have load shedding systems and/or inverters that can max out draw. A smaller 30A rig may not even have the means to even pull 30.
The 50 amp unit still can't pull more than a sustained 24 amps (80%) through a standard 30 amp breaker. If a guest is paying for 30 amp service, are you saying they can't use it? And those 'Y' adapters don't work on a current code compliant pedestal with a GFCI utility outlet. Any RV can have an inverter on board that pulls from the batteries, that's certainly not unique to 50 amp RV's. Any RV with an A/C, microwave, hair dryer or electric heater, etc., can easily trip a 30 amp breaker. If a park is seeing a significant voltage drop when full then the park infrastructure is substandard.