A/C

Dometic 15000 BTU. When running the compressor will drop off line. Sometimes after dropping off it will instantly come back on.

This happened on a trip a few weeks ago and then quit cooling. I do not know if the compressor was running when it quit cooling but I don't think it was. I normally run the fan on auto but changed it to High just to see if the coils perhaps iced up. Getting late so I shut it off for the night. Next morning started it up and it ran normally for a few hours while breaking down to move.

Just started it up in the driveway and it sounded fine. Ran it a couple of minutes the compressor dropped off and then instantly restarted. Turned unit off. Thirty minutes later I restarted and it is running fine after 45 minutes. Amp on wires running to the compressor.

Red-5.3
White-8.7
Blue 10.7
Voltage is good and steady at campground and home.
Motor start capacitor has a square device plugged onto it that says: "Motor starter WSX-7"
Compressor is quite, discharge line cold and sweaty but no ice.
Ideas?

Edited to say: 4 years old and has original Dometic digital thermostat.