I took 30 AH from my 90 AH AGM last night, not really enough to see bulk stage, and my MW can only do 41 amps anyway.
By 9 AM the solar had this battery to 13.0V
I plugged in the MW, set it to 13.9v then plugged it into the battery.
Battery was accepting 22 amps total and amps started tapering instantly.
I then bumped up voltage to 14.8v, and amps jumped upto 32, and started tapering.
Usually, I see about 1 to 4 more amps into the battery over the AH from full screen ( at ABSV) on my monitor with the flooded, when amps begin tapering.
The AGM exhibited nearly the same behavior.
If one cannot take advantage of the initial higher bulk rate many AGMs can accept, then I believe flooded will still easily win the overall $ per Cycle equation. While likely measurable, the quicker acceptance stage is likely not profound, certainly not enough to warrant spending double over flooded
Also not all AGMs say they can do Extreme recharge rates like Lifeline or Odyssey or NorthStar. Some say no more than 30 amps per 100AH of storage, which is well less than a flooded can accept. Seems these limited amp AGMs are the lower $$ AGM. Perhaps these less $$ AGM are better for low and slow all day solar, but they tend to not have the high CCA ratings, which would support large inverter loads better, nor the low self discharge rates, and are limited in bulk charging amps.
I like my AGM for its insane ability to crank my engine starter violently fast, and the higher voltages held during deeper cycling, but in the end, these mean very little, as my Flooded can still start my engine easily even when 50% discharged, and supports my maximum loads, and I consider my AGM to be an expensive 'bragging rights' battery that means little to one who does not feel the need to brag.
I could really use that 165$ extra I spent on the AGM right now versus a flooded marine battery which could perform the same tasks I ask of this AGM.
I do like the no/low maintenance aspect, as it is located in a difficult to access spot in my rig which contributed to the failures of my previous flooded banks.
Once Lifepo4 is only 2x the price of a top tier AGM, then I'll consider them, but initial outlay is the painful part for me, and for many I believe. I also want to see more data from those cycling them in RV usage. I somewhat follow the marine based Lifepo4 threads, but not so closely that I have confidence in 2000+ cycles.
Adapters of a new technology tend to want it to be superior and justify the extra expense, and perhaps this desire is enough to skew the results, if what is posted online actually represents actual results, instead of the human tendency to get others to agree with them to justify their own opinion.
I think AGM's made many similar claims over flooded back when they started becoming commonplace in boats and RV's a while back, and for the most part those 'advantages' in cycle life have not turned out to be true.
So, on the sidelines I wait for more real world testing/cycling of liFePo4, and for prices to drop, which will likely take a new latest and greatest anode/cathode technology to come to market, making Lifepo4 or LiCo as antiquated as Asphalt jarred lead acid.
How long before this happens?