gatorcq wrote:
No voltage going to furnace. Verify that 12vdc is at the reset switch.
Next the click is the thermostat relay commanding heat. 12vd should be going to a blue wire on the control board.
Don't need to info as most Atwood operate the same.
12Vdc power
12Vd from thermostat
Sail switch
O/T switch
Blower comes on
LED MUST come on Red or Green (No LED = No Power)
This is the correct troubleshooting "Follow the 12v" to the problem