Considering that nylon plugs are rated at 220psi and cpvc at 200psi, and most of us use a regulator set a 55psi or less, pressure really isn't an issue. Operating temps are 220 degrees and 200 degrees respectfully, also not to low to be a problem.
The reinforced clear plastic hose falls pretty much within the specs of cpvc, still not a problem.
I don't know what the heater thermostat is set at but I'd bet no where near 200 degrees, closer to 120 degrees.
In my mind reaching either of the max ratings of a PT valve is time to kiss your water heater and much of your plumbing goodbye.
Camco does recommend 3-5 wraps of teflon tape on the threads of the plugs.
The reinforced clear plastic hose falls pretty much within the specs of cpvc, still not a problem.
I don't know what the heater thermostat is set at but I'd bet no where near 200 degrees, closer to 120 degrees.
In my mind reaching either of the max ratings of a PT valve is time to kiss your water heater and much of your plumbing goodbye.
Camco does recommend 3-5 wraps of teflon tape on the threads of the plugs.