Notice the specs say "charging (constant voltage)" max 80a initial current.
Does this refer to bulk or abs charging?
Also, note that these are rated at 400Ah. How many multi-stage charger manufacturers/marketeers talk about bulk charging ending at around 80% soc?
It just so happens the remaining 20% of those 400Ah's is 80a... So, 80a tapering in abs/cv mode.
If the 1a:-1Ah ratio is acceptable at 80% soc, why would it not be acceptable at a much lower % soc, when charging efficiency is greater, and charging voltages and battery temps are lower?
As for temp compensating, it remains the same... simply find a suitable Vabs to maintain that 1a:-1Ah ratio, and adjust accordingly from there.