Battery Draw Bogus Math? Peukert UPDATE 2

Update- 11 Oct 20, Update 2- 12 Oct 20

Thinking one 100AH battery that can be drawn down to very low SOC gives you nearly the same "usable AH" as two regular AGM or Wet batts, as seen advertized, is bogus ?

What about Peukert? If you pick a steady amp draw like 5 amps, then that is the 20 hr rate for the 100AH batt, but is only half the 20 hr rate for the two 100s. So you would get way longer time at 5 amps with the two 100AH batts.

It is bogus to advertize that you get nearly the same AH because you can draw the one batt down so low but the other two are limited to 50% SOC using good practice. That is only because you are comparing 5 amps with 10 amps for the draw.

A "usable AH" is a clever invention indeed. :(

34 Replies

  • Useable aka Safe for the battery in question,
    Is not the same as Total Storage drain it empty
  • MrWizard wrote:
    I'm thinking your logic is Biased

    Lithium 100ah use 80ampHrs reach 20% SOC
    Recharge do it again tomorrow

    Agm or FLA 200 amp hrs, use 80 amp hrs
    Draw down to 60% SOC

    Recharge do it again tomorrow

    Which battery/bank is going to suffer the most degradation, which is going to give more hours, days, years of service,
    Which will need the lesser amount of generator run time to recharge the same 80 amp hrs

    Your statements above are only correct, If you plan draw them to zero SOC full discharge total output, and throw them away,


    My only thought was that the 80AHs are not the same running time at 5 amps. At 5 amps from the 100AH batt, that is 16 hours time.

    5 amps from a 200AH bank would be a longer running time.

    If your "use" is a 5 amp draw, then your "usable time" (vs a "usable AH") is more with the two batts.

    IMO you have to do the same activity or "use" , which is the same amps draw, to make the "usable" comparison.
  • You need to compare the actual peukert function for each battery. As the internal resistance drops there is much lower effect due to high load. Also peukert is an exponential curve. Much lower effect at anything less than the 20 hour rate.
  • I'm thinking your logic is Biased

    Lithium 100ah use 80ampHrs reach 20% SOC
    Recharge do it again tomorrow

    Agm or FLA 200 amp hrs, use 80 amp hrs
    Draw down to 60% SOC

    Recharge do it again tomorrow

    Which battery/bank is going to suffer the most degradation, which is going to give more hours, days, years of service,
    Which will need the lesser amount of generator run time to recharge the same 80 amp hrs

    Your statements above are only correct, If you plan draw them to zero SOC full discharge total output, and throw them away,