BFL13 wrote:
According to the Li graph Phil linked, you should see:
60 amper on the 100AH BB, starting at 30% SOC,
22 minutes at constant 60 amps then taper. 22 minutes at 60 is 22AH so should now be at 52% SOC for end of Bulk
If you are already tapering from 55 at the start, you must be more like 55% SOC and not the 30% you believe you are. Or the battery is really more like 60AH capacity so your 60 amper is 1C.
So pick your poison. The battery is in poor shape, or the set-up has too much R making the battery look like it has fewer than 100AH, or the monitor/meters are out of whack.
Something doesn't come out right anyway. Or they are not telling us what really goes on with a BB Li.