nvreloader
Apr 06, 2014Explorer
Best Way??
I have 4-Canadian SC6P-220w Panels with the following spec's, Pmax=220W Voc =36.60V ISC =8.09A VMP =29.30V Imp =7.52A Voc-coef =0.1281V/C Noct =45.00C 15A fuse rating/series Per actual meas...
smkettner wrote:X2
I agree, NO fuses needed on the panel side. Service disconnect maybe.
The current is self limiting. You can short the panels and no harm done.
More than two parallel technically needs a fuse.