RoyB
Dec 06, 2013Explorer III
The front panel of the Honda EU20001 says 13.3AMPs at 120VAC... That is around 1600WATTS...
I use my 2KW Honda to re-charge my three 85AH batteries in parallel using a PD9260C COnverter. I read 52-53AMPS DC Current being drawn by my battery bank for about 10 minutes then it start dropping back.
I can recharge my three batteries back up to the 90% charge state with-in a three hour run time on my 2KW Generator.
I think the PD9280 Converter input watts is around 1300WATTS at 120VAC so the 2KW Honda Generator should run that ok. IT does however state you should plug the PD9280 converter into a 20AMP receptacle, I think the 2KW Honda Generator only has a 15AMP 120VAC receptacle on it....
I suspect you do not have enough WATTAGE capability from the 2KW Honda Generator to re-charge your battery banks back up to 90% charge state in a three hour generator run time period. The rule of thumb is somewhere around 20AMPs of DC current for each battery in your bank to obtain a 90% charge state in a short three hour generator run time.
Maybe the experts will dime in here on what you need to make it work...
Roy Ken
Roy Ken
Having RV issues? Connect with others who have been in your shoes.24,405 PostsLatest Activity: Aug 12, 2026
