Ron_Nielson's avatar
Ron_Nielson
Burned Neutral Wires at the Buss in the Breaker Box
All of my neutral wires are burned at the buss at the breaker box about 2". Does this tell you anything about where a loose neutral connection is likely to be? I have read that the burnt wires need to be cut back to good copper and the buss replaced. Is that because the burned wires and buss has a higher resistance than clean connections?
The rest of the story: Trailer is a 2009 Arctic Fox 5th wheel. Only known electrical problem was probably 9 years ago plugging into a sloppy electrical pedestal at an Arkansas state park, and that burned the trailer's connector blade at the pedestal. Trailer is plugged into 120V power at the house all the time. We left KS and stopped overnight in Denver. Plugged into 120 and had power in the trailer for a few minutes, then no 120V power, so used 12V that night and went on to Ogden UT, plugged in no 120v power. Discovered that neither the 120V power nor generator power would come into the trailer, so figured that the transfer switch was bad. Changed out the transfer switch and then had 120V from both shore and generator. That's when I started smelling burning plastic smell in the breaker box. Can't say if they were burned before, but never a problem before this trip.
  • TURN OFF all power THEN feel for a warm terminal :)
    Sorry to be so grumpy in my prior post. There is only one correct answer to this and I have posted it numerous times and the response seems to be "HUH?"
    Something that can kill you is slightly more inconvenient than something that merely breaks or doesn't work right.
    The moment you get your 'new-to-you' RV home, grab a flat blade screwdriver go to the AC panel and 1 by 1 pull neutral wires and closely inspect copper wire ends. Shiny as a new penny is the rule.
    If a wire end isn't shiny it's time for a replacement buss bar. Home Depot and others sell them.
    Next, take several images of the buss before you disassemble. COUNT the number of wires.
    Dip the shiny-as-a-new-penny in silicone grease then start inserting them into the newly installed buss bar
    When you go to tighten the shiny-as-a-new-panny set screws, tighten the living scronche out of the set screws.
    When all the neutrals are done, check the hot line voltage black wires. Every last one should be tighter than hell and it's it's common to hear a 'snap' as the screw loosens. As long as the screw has been loosened pull the wire out of the breaker and check for shiny-as-a-new-penny ends. These you can scrape shiny with a sharp utility blade. dip in silicone grease and then re-install.
    After a hundred or so road miles, re-check all screws.
    You will not be dealing with this issue again. Sleep tight.
  • Is it a 50 amp service?
    If its not, it's loose connections = high resistance where the burn is. Resistant at location A does not cause a burn at location B. The problem is precisely where you see it.
    A 50 amp service, if miswired at the source, can potentially overload the neutral. So long as it's correctly wired to 220v, the neutral carries only the DIFFERENCE between the two hot wire currents.
    If the source outlet has both 50 amp sources at just 110v, the neutral will carry the SUM of the two hot wire currents. No outlet should be wired at 50 amp /110-120v but you hear occasional accounts of people who've encountered a "cheater" 50 amp plug.
  • MEXICOWANDERER wrote:
    Loose wire in RV electrical is a scandal. Holes in aluminum with set screws are NOT MEANT for fine stranded wire..
    I've used Romex for inverter wiring for years. Not as much contact surface area, but no squashing either. My Cotek 48v inverter just died, but the 120v set-screw Romex was shiny and clean.. and I run air off it regularly. Just have to wiggle the heck out of it when installing to make sure it's really in there good.
  • Your BUSS screws will appear tight because the BUSS got hot and seized some of the screws. If you have an Open/loose Neutral on a 50 amp RV, it will usually NOT burn or melt anything. It will supply 220 to the RV and burn out some appliances The Open on a 50 amp can be at the CG pedestal or on the Shore cord or at the Main electrical breaker panel. Doug
  • RVs vibrate and bounce down the road and connections become loose. All AC connections should be checked and tightened annually.
  • wa8yxm's avatar
    wa8yxm
    Explorer III
    BB_TX wrote:
    Shortly after buying our 5er I opened up the breaker panel and fuse panel and checked wire connection tightness on all hot, neutral, ground, +12, and 12 ground points. Around half the screws were not properly tightened. Would probably have experienced the same as you over time.
    Ditto. I had issues with my A/C.. Poking around one of the wires moved (NOTE I do know how to poke around safely. REMOVE POWER FIRST (Unplug) well I got out ye old screwdriver and 3 1/2 turns later.. .Was happy
    Decided it was a good time to take a tour-de-screws.
    Now I tell folks many RVers have "A few screws loose".
    I used to have a co-worker who fully agreed. but somehow I don't think we are talking about the same screws.
    I also had a loose screw on the power inlet
    And one camper I assisted had not one not two but SIX loose screws in his shore cord Outlet (The part that plugs into the RV).. Now in case you are wondering there are only six screws INSIDE that device (plus two more outside.. Those were tight)
    We got him back in business.. But I'd have loved to be a witness to the chat he had when he got back to his dealer.. You see the Trailer was so new the sticker was still in the window. .I kid you not.
  • Latest update. I cut back the burned neutrals, cleaned the grounds and every breaker now has power and nothing is overheating after 3 hours or so. THe only remaining thing is that the A/C (air contitioning) unit will turn on, run for a few minutes, then shut off, but not restart. If I recycle the breaker,fool with the thermostat, it will again start briefly ad shut off. So the original problem and subject of my original message is win and a fix, thanks to all those who tok the time to share their thoughts. And it was really quite easy. Who knew that replacing the buss and cutting back the neutral wires would work so well.
  • Throughout Quicksilver I used marine duplex tinned twin wire.
    The size No #6 uninsulated spade 12-10 gauge. This fits household receptacle screws.
    Soldered onto the 10 gauge duplex wire
    Meltable liner 1/4" shrink tubing.
    Then smothered in dielectric grease and the grease was forced into the double contact slots until it oozed out.
    When the spade terminals were slipped under the receptacle screws I tightened the scronch out of them. Bryant green dot 20-amp (hospital grade) pieces with nickel plated hardware.
    Sounds like you know what you are talking about! Good post.
    Excellent post as usual from Doug.