DrewE wrote:
bigfootford wrote:
smkettner wrote:
Dang I hope there is enough slack in the wires to cut them all back enough to make this right.
If there is not enough wire to reach a new ground buss bar there's nothing to stop anyone from leaving the bar suspended, reattach the wires and then use 1/16in X 1" or so or thicker aluminum stock. Bend it to attach to the bar and chassis of the box. That would secure it enough to be safe.
Jim
Just to be clear, this is the neutral bus bar, not the ground bus bar. You do NOT want electrical connectivity between it and the power center chassis. Doing so would introduce a ground fault and not be code compliant...and, in the event of a neutral fault or a reverse wired pedestal with a poor ground connection, could easily lead to a dangerous hot skin condition on the RV.
Good catch, just a typing brain fardt... I will correct my post...
Think the objective statement was correct, just the naming of the buss bar...
Thanks,
Jim