Slownsy wrote:
Hi all I finally got the inverter and Magnum calls for 4/0 cable 405A max fuse classT or equivalent as this has a time delay however because the fuse can be energized from both directions has to be able to disconnect power on both ends ? They picture a battery disconnect on inverter side of fuse nothing on battery side Do,they disconnect positive cable ?. I have already got a trimatic display and the 500A shunt for negative. I intend to order cables ready made and also fuse and disconnect and then have a mobile technician help with install. Any recommendations for switch and fuse appreciated. There is also some recommendations as regards to use of GFCI. Is this referring to the power points?. In Australia we use RCD relays Residual current devise but in RV also RVD as no earth stake if this makes any sense to anyone comments appreciated. We will also have a step down transformer instaled for use in Australia as we intend taking it back. Any recommendations as for good technician in Fort Myers, Naples etc FL. Thanks.
Frank
As to a Battery disconnect. I HAVE NEVER SEEN A RV INVERTER/CHARGER WITH A BATTERY DISCONNECT INSTALLED FOR THE INVERTER BATTERY CABLE CIRCUIT. There is NO need unless you want to be able to positively disconnect the Batteries to keep from draining them. But, turning the Inverter OFF will stop parasitic drains. So, as I stated no need for a battery disconnect. The 200/250/300 amp fuse on the Positive cable is a protection for the cable from the batteries in case of short. NOT a protection from the Inverter to the batteries. You want that fuse as close to the Batteries as possible. Doug