Calculating voltage drop

In determining which size wire to use, what load do we enter when calculating voltage drop when adding a 50 amp RV site when the electric service is a 240 volt, 50 amp breaker and RVs technically run on 120 volts? Do we count the RV as 50 amps, or can we count it as just 25 amps since the RV essentially has two 120 volt, 25 amp circuits?
  • 50A is 240/120V 4 wire which is used as 2x 50A circuits. 240V appliances are not the norm for a RV. The 2 hot wires and neutral are each rated for 50A which is the maximum. ie You have a total of 100A @ 120V for the 2 circuits or 12KW.

    Use 50A load for the wires which are normally 6ga unless long distances are involved.
  • I'm not following. What do you mean 'which wire', and what does voltage drop have to do with it?
  • I don’t know if your RV is somehow different, but generally, 50A RV’s are two 120 volt 50 amp circuits.