Coleman Airxcel 48000 series 15KHP

My rig is going on 6 years old in March. The rear roof hvac unit is an Airxcel 15k heat pump and has work well until now.
We were in NE GA at the end of October and used the heat pump in cold weather just fine until needing to switch to the furnane.
In route home, we stopped S of Atlanta and stopped overnight (55 degree weather) and I switched on the heat pump. It ran but no heat.
The RV has been parked at home since until today. We arrived at our destination and no heat. 62 dgrees outside. I switched to ac and lowered the thermostat. The unit came on but was only blowing ambient air.
So the unit will run with the thermostat set to either mode but will not cool or heat.
I ordered and have received the run capacitor and will try to swap it this weekend.
This unit has 2 capacitors. One is the run capacitor and the other the fan. The fan is running in both modes so I assumed its ok. There is also another part in the that the parts diagram shows called a "OD Temp Relay Board" which looks like a clear covered relay.
I ordered the run capacitor and replaced it last weekend. No change at all.
I'm not an electrician or electronics guru but do have mechanical abilities. I read up on discharging capacitor prior to replacing them. When I attempted to discharge the original capacitor, I did not see or hear any spark.
I assume the fan capacitor is ok since the fan will run in both modes so it has not been replaced.
I ordered the relay and a fan capacitor as well and hope to get those replaced in the next few days starting with the relay.
Any suggestions in the meantime would be appreciated. Thanks.
  • There is a compressor relay on the upper control board. You disconnect 120 power and then jump the 2 wires. Verify 120 volts on the jumped wires. IF the compressor comes ON, then your control board relay is probably bad. This just verifies that the Capacitors and Compressor runs. You may still have a 12 volt control problem activating the compressor relay. There is a 12 volt connection on the control board that when 12 volts is supplied will activate the relay. Supply 12 volts to the "Y" terminal should activate the relay. If you do NOT have 12 volts at the Y when trying Heat or Cool, then either the wall tstat is bad or the Y wire from the tstat to the upper control board is open. Doug
  • Thanks Doug. I replaced the entire control board and run capacitor. I ordered the relay but its is not the correct one nor can I find it. I have not replaced the thermostat but I do hear the thermostat click when the unit comes on and sends the temperature set-point. Thanks.
  • Heres a pic of the relay that I cannot find anywhere on line. I ordered the part number list in the Airxcel parts list, however, it does not have enough terminals.
  • Is this the one

    https://pdxrvwholesale.com/products/coleman-air-conditioner-relay-1460-1271
  • Thanks. I ordered that part number right from the manual. It came but it does not have enough terminals. The one in the unit says 06x13 at the bottom. The one sent says 03x18 and does not have enough terminals. So odd but then again, not really. LOL